Just who is recommending this and what is your application?it was recommended to use 60 amps circuit breaker and wire size 6 AGW with a 240-volt NEMA 14-50 outlet but Nema 14-50 is designed for 50 amps circuit breakers?
The motor exception is for when using the plug as the motor controller and applies to 1/3 HP and less motors210.20 (1) Single Receptacle on an Individual Branch Circuit. A
single receptacle installed on an individual branch circuit shall
have an ampere rating not less than that of the branch circuit.\
(2 exceptions --welders & motors)
Just who is recommending this and what is your application?
Tesla presentation to the customersJust who is recommending this and what is your application?
I think there is a misunderstanding between the customer and Tesla. The plug in Tesla charge cords can be connected to a maximum 50 amp breaker. If this is a wall charger it can get connected to a larger circuit (up to 100 amps) but the wall chargers are hard wired not plug in.Tesla presentation to the customers
Presuming the item is listed and instructions are a part of the listing.The NEC requires you to follow the manufacturers instructions. How ever "Perplexing" they may be,![]()
Yeah and oddly the motor one goes away if the circuit supplies two or more receptacles, but the welder one stays 210.21(B)(3)210.20 (1) Single Receptacle on an Individual Branch Circuit. A
single receptacle installed on an individual branch circuit shall
have an ampere rating not less than that of the branch circuit.\
(2 exceptions --welders & motors)
Just land it on a 2 pole 50A breaker, What is the load/FLC?it was recommended to use 60 amps circuit breaker and wire size 6 AGW with a 240-volt NEMA 14-50 outlet but Nema 14-50 is designed for 50 amps circuit breakers?
Does NEC say only follow the instructions if the item is Listed?Presuming the item is listed and instructions are a part of the listing.
When it comes to what we are discussing here, a NEMA standards receptacle will very likely comply with both NEMA standards as well as any listing requirements.Does NEC say only follow the instructions if the item is Listed?
If a recept comes w/o instructions and w/o a Listing, but has on the plastic "50A 240V", when would NEC allow that item to be on a 60A BC? The AHJ should balk on that, no?