I agree with the others.
Other than the Elevator (which would be fed from a separately metered House Panel), water heaters and condensing units are probably the only strictly 240v loads that could safely use the wild leg anyway.
Not worth the risk or the expense of extending the 120/240v 3ph delta to the apartment panels just for those.
You would also loose a lot of space in a 3 phase tenant panel in circumstances like this just trying to avoid the wild leg on the circuits that couldn't utilize it.