tran1336 said:
But just common sense, how can you hard wired a piece of equipment that on wheels.
The wheels are probably not the issue.
You said this is a "big freezer" in a commercial building. Common sense is that it will be very heavy, and moved only to clean to satisfy health department regulations, that is, moved only infrequently and only just enough to get behind / under it.
The real question, in my mind, is where the point is that the wiring from the wall (Premises Wiring System
: see Article 100 Definitions) ends and the wiring in the freezer (Utilization Equipment
: see Article 100 Definitions) begins.
The NEC only covers the wiring up to the edge of the Premises Wiring System.
If the freezer comes with a flexible conduit whip (not likely) the whip can be part of the freezer, the utilization equipment.
But, more likely, the flex was installed to the freezer by the electrician, making the end of the flex that connects to the freezer the "edge" of the Premises Wiring System, and placing the flex whip under the NC.
Looking at 348.30(A) and 348.30(A)
Exception No. 2 I would check the freezer whip to see that the various lengths are within the limits.