Back on topic.
Picture a typical wood framed home, I run a 12/2 and a 14/2 NM from the panel to a two gang box in the kitchen, the 12/2 supplies the SABC and the 14/2 supplies the lighting, all the EGCs in this box must be connected together (250.148) so that will put a 14 and 12 AWG copper EGC in parallel. This is common and not a violation.
I agree. Even EGC's from two different panels or two different services would still be connected together in a box if they both existed there.