Can you put a two pole breaker on the high leg for a high delta panel
Cartoon1
Florida
Electrical Engineer
Would you be able to put a 2 pole branch breaker 240V rated on a high leg delta panel, Leg A,B or leg C,B (assuming the high leg is B)? if for example the load requirement is a 3 wire single phase? Thank you
1) A true 240V straight rated 2 pole breaker then it is fine on the high leg, but watch out, many (most??) are 'slash rated' 120/240V, whereas 3 pole breakers are often fully rated.
2) If the load requires 3 wire single phase, that implies a that it uses the neutral, which would not be fine on the high leg.
-Jon
And wholesale houses may not stock a fully rated breaker and they are a lot more expensive. A slash rated breaker on a high leg is not rated to withstand the the higher voltage in a short circuit
Expensive enough they might even be higher cost than a three pole breaker. Not because it cost more to make but is just a supply/demand thing driving the price.
Anyone have any cross section photos showing the internal differences?
Thanks,
Wayne
How much more expensive are we talking about? 200 - 300%?
I didn't keep any but I autopsied some QOs back when we had an issue with corrosive fumes at a dairy. They didn't appear any different that I can remember.
The difference is in the line to ground clearances and path for clearing the products of arc interuption.
I appreciate everyone answers. They were all spot-on, helpful, and detailed. Great community!!
For siemens, the straight rated 2 pole breakers have an R as a suffix, for example a two pole 20 is a Q220R. There arent very many hits on the internet, but I found one for $65. Their use seems to be extremely rare in my experience. Most people seem to either not know about the issue, or dont care. I run across a lot of high leg delta where I am and I dont recall actually EVER seeing a stright rated 2 pole used where required.
Another option, if this is a bolt on panelboard, is to use a 277/480 breaker. For example with siemens this would be a BQD220. I wouldnt be at all surprised if that breaker is actually cheaper than the R breaker.
Three pole breakers are usually straight 240 rated so you would think those are built to same specifications, if one wanted to take something apart to see any differences.