Expensive enough they might even be higher cost than a three pole breaker. Not because it cost more to make but is just a supply/demand thing driving the price.And wholesale houses may not stock a fully rated breaker and they are a lot more expensive. A slash rated breaker on a high leg is not rated to withstand the the higher voltage in a short circuit
Anyone have any cross section photos showing the internal differences?And wholesale houses may not stock a fully rated breaker and they are a lot more expensive. A slash rated breaker on a high leg is not rated to withstand the the higher voltage in a short circuit
I didn't keep any but I autopsied some QOs back when we had an issue with corrosive fumes at a dairy. They didn't appear any different that I can remember.Anyone have any cross section photos showing the internal differences?
Thanks,
Wayne
Good Point, thank you!!When you say 3 wire single phase that is a red flag. Is a neutral needed?
How much more expensive are we talking about? 200 - 300%?And wholesale houses may not stock a fully rated breaker and they are a lot more expensive. A slash rated breaker on a high leg is not rated to withstand the the higher voltage in a short circuit
The difference is in the line to ground clearances and path for clearing the products of arc interuption.I didn't keep any but I autopsied some QOs back when we had an issue with corrosive fumes at a dairy. They didn't appear any different that I can remember.
For siemens, the straight rated 2 pole breakers have an R as a suffix, for example a two pole 20 is a Q220R. There arent very many hits on the internet, but I found one for $65. Their use seems to be extremely rare in my experience. Most people seem to either not know about the issue, or dont care. I run across a lot of high leg delta where I am and I dont recall actually EVER seeing a stright rated 2 pole used where required.How much more expensive are we talking about? 200 - 300%?
Three pole breakers are usually straight 240 rated so you would think those are built to same specifications, if one wanted to take something apart to see any differences.The difference is in the line to ground clearances and path for clearing the products of arc interuption.