can you run pvc in the drop cealing of a pleanum return?

Status
Not open for further replies.

desanno1

New member
i have a job in long island new york and , would like to use 4" pvc to pull the communication wires threw , the wires are plenum rated, but a rival contractor saw the pvc in the drop cealing and and made a big mes for me, can anyone tell me if it is ok to run pvc in the drop cealing if a plenum return exists? and what artical in the 2005 code i can find it in so i can either fix this problem or make this contractor happy. please help!
 
If it is a plenum used for environmental air. No,you can't run PVC.
see 300.22.B
 
You can't run ridged non-metallic conduit (PVC) in a suspended ceiling that is used for return air. Take a look at 300.22(C)(1) Other spaces Used for Environmental Air.

300.22(B) is for actual ducts or plenums, a suspended ceiling that is used to convey return air would fall under 300.22(C) "Other Spaces Used for Environmental Air".

Chris
 
raider1 said:
You can't run ridged non-metallic conduit (PVC) in a suspended ceiling that is used for return air. Take a look at 300.22(C)(1) Other spaces Used for Environmental Air.

300.22(B) is for actual ducts or plenums, a suspended ceiling that is used to convey return air would fall under 300.22(C) "Other Spaces Used for Environmental Air".

Chris

oops! Yeah,That too!
 
Is this return air ducted? Not to confuse the subject but it does make a big difference if it is ducted or not. If it is ducted then the space surrounding the duct is not considered as a return:confused: air environment, just the space inside the ducting is.
 
Terrynistler said:
Is this return air ducted? Not to confuse the subject but it does make a big difference if it is ducted or not. If it is ducted then the space surrounding the duct is not considered as a return:confused: air environment, just the space inside the ducting is.

Good point, in re-reading the OP this might just be a suspended ceiling and not "Other Spaces used for Environmental Air".

If this space above the suspended ceiling is not used to convey return air then PVC is allowed.

Chris
 
raider1 said:
If this space above the suspended ceiling is not used to convey return air then PVC is allowed.

Chris

It does sound like there is a separate duct for the cold air return but I am curious-----

Chris , is it always true that PVC is allowed in a ceiling if it isn't a plenum or does the fire rating of the building also come into play at times?
 
Dennis Alwon said:
It does sound like there is a separate duct for the cold air return but I am curious-----

Chris , is it always true that PVC is allowed in a ceiling if it isn't a plenum or does the fire rating of the building also come into play at times?

I am not aware of any NEC code section that prohibits the use of rigid nonmetallic conduit above a suspended ceiling that is not used to convey return air. I looked through 352.10 and PVC is permitted to be installed either concealed or exposed where not subject to physical damage if identified for such use.

Chris
 
Pvc

Pvc

I had a plumbing buddy that ran PVC plumbing in a air handling ceiling. He found a wrap for his piping and satisfied the building inspectors. A possibility ?
 
raider1 said:
I am not aware of any NEC code section that prohibits the use of rigid nonmetallic conduit above a suspended ceiling that is not used to convey return air. I looked through 352.10 and PVC is permitted to be installed either concealed or exposed where not subject to physical damage if identified for such use.

Chris

I was thinking more in line with building codes. Plastic toxcity, blah,blah,blah

Edit to add: The reason I ask is because I don't think I have ever seen PVC conduit in a commercial ceiling. I don't get around commercial much anymore so I probably am way off on this one.
 
Last edited:
Dennis Alwon said:
I was thinking more in line with building codes. Plastic toxcity, blah,blah,blah

I am not aware of any building code that would prohibit PVC in the space above a suspended ceiling that wasn't being used for conveying environmental air.

Chris
 
Dennis Alwon said:
I was thinking more in line with building codes. Plastic toxcity, blah,blah,blah

Edit to add: The reason I ask is because I don't think I have ever seen PVC conduit in a commercial ceiling. I don't get around commercial much anymore so I probably am way off on this one.

I'm with you on this one Dennis. PVC inside a building is a ? for me. I'm not a code guru like a lot of you, so this is just a raised eyebrow comment.
 
hardworkingstiff said:
I'm with you on this one Dennis. PVC inside a building is a ? for me. I'm not a code guru like a lot of you, so this is just a raised eyebrow comment.

I haven't seen it done in commercial either, but the IBC and the NEC permit it.

Chris
 
pvc in building

pvc in building

I have always been taught that you cannot run pvc in the ceiling of a building. I was taught that pvc burning releases chlorine gas I have been working commercial in the long island area for about 30 years and have rarely seen it in commercial buildings. As soon as you penetrate the building you must switch over to emt or something else. For network and telco wires we usually provide about a 2foot emt sleve through walls with connectors and bushings on both sides, with penetrations firestopped after pipe is placed in wall
 
Last edited:
quogueelectric said:
I have always been taught that you cannot run pvc in the ceiling of a building. I was taught that pvc burning releases chlorine gas


I believe this is the reason PVC is not allowed in a Plenum Ceiling. I am not sure if it is chlorine gas but a toxic gas nonetheless
 
I agree. I have rarely seen it used and the exact reason is that if there were a fire then the burning pvc would put off toxic gasses that would incapacitate a person and therefore they would be rendered helpless to escape from the otherwise survivable fire.

I find this funy though also being a master plumber since we are allowed to run PVC water piping and DWV. In most of my experience it is side by side.

I do not do a lot of commercial though and can't give you a definitive answer.
 
I find this funy though also being a master plumber since we are allowed to run PVC water piping and DWV.

Correct, you can run PVC, PEX, ABS, PB ect in a commercial building, so why would electrical PVC be any different. You can't install these types of pipe in suspended ceilings that are used to convey enviromental air due to the flame and smoke charatistics, but they are allowed in regular suspended ceilings.

Chris
 
raider1 said:
Correct, you can run PVC, PEX, ABS, PB ect in a commercial building, so why would electrical PVC be any different. You can't install these types of pipe in suspended ceilings that are used to convey enviromental air due to the flame and smoke charatistics, but they are allowed in regular suspended ceilings.

Chris


Ty Chris, That answers my question.
 
I just finished up a three story office building. All the ceilings were plenum rated. Why can the plumber run PVC for his DWV, but I can't use any PVC in that same plenum rated ceiling???
 