Okay, so let me play devil's advocate here... :angel:It is not. Minimum circuit ampacity are branch circuit selection current are separate items.
Take a look at 440.32, for instance. MCA is determined by 125% of the RLA or 125% of the BCSC, whichever is greater.
Where does nameplate MCA come into play in Article 440... or does it not and is simply compliance 110.3(B)?
____
Also seems redundant for requirements such as 440.32 (there are several in Article 440) that state "the motor-compressor rated-load current or the branch-circuit selection current, whichever is greater." The definition in 440.2 states "The value of branch-circuit selection current will always be equal to or greater than the marked rated-load current." Seems to me it should be stated as "the motor-compressor rated-load current, or the branch-circuit selection current if so marked."
Nevertheless, I'm the same as you in that I've never seen a unit with BCSC on the nameplate... :happyno: