can you use a switchgear room for storage

Status
Not open for further replies.

firelient

Member
Location
Staunton,VA
I thought I found in the code somewhere that you could not use a switchgear room for any storage. It is a 4000a service with about 8' in front of cabinet.with one engress.I looked in Artical 110 and didn't see anything. Can any of you help me or was i dreaming. Thanks
 
Just maintain your working space requirements, and you're good to go. Put whatever you want to in there that isn't in the required working space zone(s).
 
Here's what typically happens:

9910.jpg
 
firelient said:
I thought I found in the code somewhere that you could not use a switchgear room for any storage. It is a 4000a service with about 8' in front of cabinet.with one engress.I looked in Artical 110 and didn't see anything. Can any of you help me or was i dreaming. Thanks
(I bolded some of your key points)

I think 110.26(C)(2)(b) addresses this location:

2005 NEC said:
110.26
(C) Entrance to Working Space.
(1) Minimum Required.
At least one entrance of sufficient area shall be provided to give access to working space about electrical equipment.

(2) Large Equipment.
For equipment rated 1200 amperes or more that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to the required working space not less than 610 mm (24 in.) wide and 2.0 m (61⁄2 ft) high at each end of the working space.
Where the entrance has a personnel door(s), the door(s) shall open in the direction of egress and be equipped with panic bars, pressure plates, or other devices that are normally latched but open under simple pressure.
A single entrance to the required working space shall be permitted where either of the conditions in 110.26(C)(2)(a) or (C)(2)(b) is met.

(a) Unobstructed Exit.
Where the location permits a continuous and unobstructed way of exit travel, a single entrance to the working space shall be permitted.

(b) Extra Working Space.
Where the depth of the working space is twice that required by 110.26(A)(1), a single entrance shall be permitted. It shall be located so that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition.
 
Now, at the other end of the scale...

Now, at the other end of the scale...

...we have electrical / mechanical rooms that many can only dream of!

DSC04708a.jpg


DSC04709a-1.jpg
 
Thanks for the input. I'm trying to keep our room from looking like the other rooms. I will try and talk them into it by the working clearance wish me luck
 
fwiw (and you may already be aware), there are building codes which deal with the storage issue, and the fire marshals particularly frown on it, so you might want to check your local codes for more support.
 