To step up a 3 phase 208V to a 3 phase 480V, can you use a 208V delta to 480V wye transformer and just not connect the neutral? Is this allowed?
Let me explain what I'm trying to do.
We have a 3 phase 208V supply and need 480V for a motor. Would it make sense to do 208V delta to 480V delta? Or do 208V delta to 480V wye (and just not connect the neutral since it is not needed for a motor load).
Yes. Do this..... Or do 208V delta to 480V wye (and just not connect the neutral since it is not needed for a motor load).
If you haven't purchased the transformer get a 208 delta to 480 delta.
Then your electrician wont be calling asking what to do with XO.
Yes. Do this.
A delta, wye step up transformer gets wired the same as a step down transformer. You bond the XO at the transformer or first disconnect and don't bring it to the motor, but you will have 277V to ground in case of a ground fault instead of 480V.
If he does I would call someone else. 480V is not something you want someone to practice on.If you haven't purchased the transformer get a 208 delta to 480 delta.
Then your electrician wont be calling asking what to do with XO.
And gotta attach XO to the GES, 250.30(A)(4) and (5) right?
Same place the bonding jumper for XO is connected.
Correct. I was focused on the neutral because that's what the discussion was revolving around.
True, he won't be asking what to do with X0 but it will create a whole host of other code issues to consider that are far more complex than using a 208 delta X 480Y.
I don't see what is so complex. The secondary needs to have a conductor grounded. Since the neutral isn't used as a circuit conductor you possibly may be able to ground a phase conductor, but why not bond the neutral and have 277 volts to ground instead of 480 - you won't use any more or less copper either way?True, he won't be asking what to do with X0 but it will create a whole host of other code issues to consider that are far more complex than using a 208 delta X 480Y.
You are making texie's point that is simpler to ground the neutral of a wye secondary.True, he won't be asking what to do with X0 but it will create a whole host of other code issues to consider that are far more complex than using a 208 delta X 480Y.
I don't see what is so complex. The secondary needs to have a conductor grounded. Since the neutral isn't used as a circuit conductor you possibly may be able to ground a phase conductor, but why not bond the neutral and have 277 volts to ground instead of 480 - you won't use any more or less copper either way?
If you don't solidly ground one secondary conductor then you need a ground fault detection system, so unless it is a process that you want an orderly shut down if a fault occurs, you are going to spend less by grounding that system. High impedance ground is one other option if you do have a wye secondary, but has similar costs and issues as the ungrounded system.
You are making texie's point that is simpler to ground the neutral of a wye secondary.
I never heard of a 208 volt delta transformer. could someone draw a diagram ?
And the fact that the transformer has a delta wound primary does not prevent you from connecting it to a 208Y/120 source.Here is a datasheet for 208V Delta to 480/277V wye step up transformers:
http://attachments.temcoindustrialpower.com/Data_sheet/Federal_FH_3Ph_208_480Y277.pdf
Note the wiring diagram has H terminals for the secondary higher voltage side, so you have an H0 terminal that should be bonded.
-Jon