2017 NEC
220.18 Maximum Loads.
(B) Inductive and LED Lighting Loads. For circuits supplying lighting units that have ballasts, transformers, autotransformers, or LED drivers, the calculated load shall be based on the total ampere ratings of such units and not on the total watts of the lamps.
Trying to determine the rating for the canless led that have integral driver. Listing on sales pages only show wattage of lamp. Seen listing of lighting with separate drivers that show lamp wattage and driver amperage separately.
Looking for how to determine compliance with above code.
220.18 Maximum Loads.
(B) Inductive and LED Lighting Loads. For circuits supplying lighting units that have ballasts, transformers, autotransformers, or LED drivers, the calculated load shall be based on the total ampere ratings of such units and not on the total watts of the lamps.
Trying to determine the rating for the canless led that have integral driver. Listing on sales pages only show wattage of lamp. Seen listing of lighting with separate drivers that show lamp wattage and driver amperage separately.
Looking for how to determine compliance with above code.