W wmeek Senior Member Location Texas Occupation Electrician Apr 14, 2008 #1 Can you use 8' strip flourescent light fixtures under a canopy. They are rated for dry locations only. Had a canopy company install a canopy and the light fixtures. I felt they needed to be for damp location. Thanks
Can you use 8' strip flourescent light fixtures under a canopy. They are rated for dry locations only. Had a canopy company install a canopy and the light fixtures. I felt they needed to be for damp location. Thanks
iwire Moderator Staff member Location Massachusetts Apr 14, 2008 #2 I would start in Article 100 "Locations, Damp" then move onto 410.4(A) It sounds like a violation to me.
I would start in Article 100 "Locations, Damp" then move onto 410.4(A) It sounds like a violation to me.