I agree, if the field wiring was correct and compliant as 2 separate MWBCs (1,3,5 and 7,9,11) then there is no reason to change the field wiring in order to combine the circuits.
Rather than supplying all of the original 1,3,5,7 conductors from breaker 1, I would have supplied 1 and 7 from breaker 7...3 and 9 from breaker 9, and 5 and 11 from breaker 11.
This would free up the same number of breakers, keep loads distributed on the supply phases and on the field neutrals, keep the facility color code intact, and possibly save a wirenut
-Jon
I disagree.
If you did that you'd still have to change the neutral connections in the field or you would be creating parallel return paths since the return current would be coming back on 2 different neutrals.
For example:
if you turned on breaker 7 as you have it, the return current from circuit 1 would be coming back on the original neutral for 1,3 &5 and the return current for circuit 7 would be coming back on the original neutral for cirucuit 7,9 &11.
JAP>