What is the minimum size THW,or THHN conductor that can be used to wire an 80 kvr,3/0 460 volt Cap.
Help me on this one . Mike doesn't have anything in the work book.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Try this formula to find the current then use the reference 460.8 to find the minimum conductor ampacity.

I=kva/(E * 1.73)
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
that is what I got.

Start by converting 80kVA to amps

I do either POCO calcs. or residential only.
The POCO calcs are a little different that NEC calcs. With that said, I want to see if I can get this right. Jumper, 135.7? Which comes out to 1/0. (75?) Yes or try again...
 

Flight987

Senior Member
I Did some Cal.

I Did some Cal.

I took 80000/(460x1.732 =796.72) So 80000/796.72=100.41 Amps. So 460.8 said thing's I don't understand.
I don't get this at all. Your turn.
 

jumper

Senior Member
I took 80000/(460x1.732 =796.72) So 80000/796.72=100.41 Amps. So 460.8 said thing's I don't understand.
I don't get this at all. Your turn.

Use 480V not 460.

460.8 says that the capacitor supply wires must be 135% of capacitor load rating, so multiply your number by 1.35 and then pick a conductor from 310.16.
 
Last edited:

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
What is the minimum size THW,or THHN conductor that can be used to wire an 80 kvr,3/0 460 volt Cap.
Help me on this one . Mike doesn't have anything in the work book.

Use 480V not 460.

.

OP said 460V. IMO, you can use that kind of like you are allowed in TBL 430.250. But it comes out the same either way.:thumbsup:
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Maybe, I was taught to always use the listed nominal voltages for calcs. IDK.

It's not written/stated under the capacitor section but it seems similar since caps are often used in a motor circuit. The motor FLC tables state that you can/are permitted to use system voltage ranges of 110-120, 220-240, 440-480V, etc.
If the OP used either 460v or 480V it still works out. If he can grab hold of the basic formula that is.

Edit:I was wrong, if you use 480V instead of 460V you get 129.91 and you could use #1 for that. But since he said answer key said 1/0, they must have meant to use the actual 460V in the question. That would give you the 1/0 answer. (135.55A)
 