bphgravity
Senior Member
- Location
- Florida
Section 422.31(B) of the 2005 NEC has added a sentence to clarify the allowance of a lockable switch or circuit breaker being used as the disconnecting means for the appliance.
It now basically states that the means for locking the swirch or circuit breaker must be installed and must be kept in place to qualify. This clears up the 2002 NEC where the wording implied the locking means and loack didn't necessarily need to be there at the time of installation. It just need to be capable of being locked at the point it was being used as a disconnect.
Can we assume that every section in the NEC that permits a switch or circuit breaker to qualify as the disconnecting means if capable of being loacked should also meet this provision, or does the intent not spread beyonf that of appliances over 1/4hp or 300VA?
It now basically states that the means for locking the swirch or circuit breaker must be installed and must be kept in place to qualify. This clears up the 2002 NEC where the wording implied the locking means and loack didn't necessarily need to be there at the time of installation. It just need to be capable of being locked at the point it was being used as a disconnect.
Can we assume that every section in the NEC that permits a switch or circuit breaker to qualify as the disconnecting means if capable of being loacked should also meet this provision, or does the intent not spread beyonf that of appliances over 1/4hp or 300VA?