OK I have leaned some more, I ended up talking with the guy who installed this capacitor and was there when the fault happened. The reason I could not find a problem is that the bad capacitor bank has already been removed and the one I was looking at has never been energized.
weressl said:The harmonics are surprisingly high. Where would they originate from in a relatively benign system?
Is this a parralel resonant circuit being formed by load inductors(motors) and the cap bank??At the point of resonance, the voltage across the capacitor rises towards infinity causing the capacitor to fail. It is a frequency thing not an applied voltage issue.
I took it that the wires were disconnected from the breaker and Bob was checking things out and getting some suggestions as to what to look for/check prior to hooking it back up.
So what was the original failure mode?
That's why individual PF correction at each motor, though costly and somewhat impractical, may be the way to go.
Either that or put up with repeated failures of this cap bank.
If I was in your position, I would hook the bank back up and throw the breaker..from a safe distance just in case.![]()
How about from all the computers in the check stands and the barcode scanners and inventory systems? And maybe even electronic ballasts.![]()
Bob, if you want to do a bit of work, you could always separate the leads, energize one cap (or small group) at a time at first, then connect them all back together.Breaker turned on for the first time and immediately there was fireworks, then darkness then the generator came on line. Then my to buddies had to go change their shorts.
But it is not an option that is even remotely going to happen.
After talking with the guys on the scene it is my opinion the cap was shipped with a fault and my buds where lucky they closed all covers tight before they turned it on.
Cutler Hammer replaced the unit free of charge without explanation of the cause.
That is pretty much where I am heading but I will see what data is recorded for a week.
Pretty new store, mostly florescent lighting with electronic ballasts along with all the other items mentioned.
Breaker turned on for the first time and immediately there was fireworks, then darkness then the generator came on line. Then my to buddies had to go change their shorts.
But it is not an option that is even remotely going to happen.
After talking with the guys on the scene it is my opinion the cap was shipped with a fault and my buds where lucky they closed all covers tight before they turned it on.
Cutler Hammer replaced the unit free of charge without explanation of the cause.
That is pretty much where I am heading but I will see what data is recorded for a week.
Pretty new store, mostly florescent lighting with electronic ballasts along with all the other items mentioned.
As compared to what? The voltage THD looks ok and as for the currents, I suspect when iwire gets the ISC/IL ratio, that they will fall close to, if not within, acceptable limits.The harmonics are surprisingly high.
zzzzzzzzzzzzzzzzzThat is pretty much where I am heading but I will see what data is recorded for a week.
That is funny how a manufacturer will do that. I just saw a "How It's Made" episode where they said the # of stitches the manufacturer put in the glove was a trade secret.:-? Ummm, here's another trade secret: most of us can count.I've noticed that some don't adequately inform people of what's inside, they think it's some sort of super trade secret or something.
zzzzzzzzzzzzzzzzz
Different issue.
You mentioned that this is a new store and only has typical fixtures and refrigeration. But a lot of newer refrigeration compressors are now coming with VFDs built in by the manufacturers.
I just saw a "How It's Made" episode where they said the # of stitches the manufacturer put in the glove was a trade secret.:-? Ummm, here's another trade secret: most of us can count.
No VFDs in this store and the stores I work in that have them they are almost all in bypass mode by the end of the first year.
Curious as to why?