Not knowing which Elec car a customer is getting, should we run 3 or 4 wires? They want 60 amp capacity. Thank you.
I picked beef on the invitation......If you're not sure how many are coming to dinner, 3 or 4, how much chicken do you buy?
Ok, Krystal or White Castle?I picked beef on the invitation......![]()
An EVSE is 240V only, so if it is hardwired, 2+1 will do. Some plug in EVSEs use a NEMA 14 plug, in which case you need a neutral for the NEMA 14 receptacle. But I believe that at 60A it will be hard wired.Not knowing which Elec car a customer is getting, should we run 3 or 4 wires? They want 60 amp capacity. Thank you.
Unless it is an early Eaton, but yes, the vehicle itself is 208-240 only.An EVSE is 240V only, so if it is hardwired, 2+1 will do. Some plug in EVSEs use a NEMA 14 plug, in which case you need a neutral for the NEMA 14 receptacle. But I believe that at 60A it will be hard wired.
Cheers, Wayne
Not knowing? 3 wire with ground 60amp or larger circuit.Not knowing which Elec car a customer is getting, should we run 3 or 4 wires? They want 60 amp capacity. Thank you.
The Tesla charger has no place to connect a 4th wire.Note knowing? 4 wire 60amp or larger circuit.
That is true of all the Teslas I've installed.The Tesla charger has no place to connect a 4th wire.