Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
Do car charger outlets need to be gfci ? Thank you very much? Thanks for your help, much appreciated
Well, according to 2020NEC 625.54, and 625.60(D), yes. Does the manufacturer's instructions say otherwise?
The Commentary in the handbook discuss that yes, as you said... the receptacles suppling portable or fixed in place cord and plug charging systems require GFCI. However, it also states, in agreement with you, that direct connected systems are not required to have GFCI unless specified by the manufacturer.Those require GFCI only for receptacle outlets, not all outlets.
The Commentary in the handbook discuss that yes, as you said... the receptacles suppling portable or fixed in place cord and plug charging systems require GFCI. However, it also states, in agreement with you, that direct connected systems are not required to have GFCI unless specified by the manufacturer.