Hey guys , this is something I have never done before. Does a 50 amp Rec. for a Tesla have to be fed from a gfi breaker if installed on the outside of a house? In the literature it says no but I'm thinking that was meant for indoor.
The NEC does not require GFCI protection for 50 amp receptacles.
Correct, so the installer doesn't have to provide it but does 625.22 require the supply equipment to provide it?
Kinda reads that way.... Not sure.
Yes, the EVSE provides GFCI (within 12" of the plug), you don't need to provide it for the receptacle itself.Correct, so the installer doesn't have to provide it but does 625.22 require the supply equipment to provide it?
Yes, the EVSE provides GFCI (within 12" of the plug), you don't need to provide it for the receptacle itself.
Cheers, Wayne
Yes, the EVSE provides GFCI (within 12" of the plug), you don't need to provide it for the receptacle itself.
Cheers, Wayne
625.22 basically states the charging equipment must have the protection built in.
It does not require the circuit or the receptacle to be GFCI protected.
That's what I thought.
Sorry that the others got lost on the question.........