Anyone know a number of cat 5 cables that can be run in 3/4" ,1" ,1 1/4" and 1 1/2" PVC Sch 40??
mdshunk said:568: 4.4.2.6.3 ?Boxes shall be placed in a straight section of conduit and not used in lieu of a bend.? (no angle or U pull boxes)
569: 4.4.2.1 ?No section of conduit shall be longer than 30m (100ft) or contain more than two 90 degree bends between pull points or pull boxes."
Not really. When you need your third bend, you put a straight through pull box right before (or shortly before) the third bend, and your bend count "resets". If this is an underground run, you install a handhole type enclosure with a mousehole in each end every 100 feet. Underground, you can "curve" the pipe over the entire run and maybe not need any bends, per se. One long curved run with a couple hundred foot radiused bend.Shockedby277v said:These 2 will be hard to accommodate. Wow, thnx for the info.
I would interpret 568: 4.4.2.4 to mean that you cannot have more than three outlets/jacks on a given cat5 cable rather than not more than three cat5's in a given conduit.mdshunk said:For your Cat5, the TIA-EIA 568 and 569 requirements are much more strict than the NEC. Here's a couple to see if they help:
568: 4.4.2.4 ?Any single run, extending from a telecommunications closet shall serve no more than three outlets.? (an outlet can be a single jack on a plate. even if you ran 4", you can only have 3 cables in it)
568: 4.4.2.6.3 ?Boxes shall be placed in a straight section of conduit and not used in lieu of a bend.? (no angle or U pull boxes)
569: 4.4.2.1 ?No section of conduit shall be longer than 30m (100ft) or contain more than two 90 degree bends between pull points or pull boxes."
569: 4.4.2.2 ?The inside radius of a bend in a conduit shall be at least 6 times the internal diameter. When the conduit size is greater than 50mm (2 inches), the inside radius shall be at least 10 times the internal diameter of the conduit. For fiber optic cable, the inside radius of a bend shall always be at least 10 times the internal diameter of the conduit?
Except for that fact that the spec is in the raceway section, and the "run" they are talking about is a run of raceway. Sorry for the confusion. I was trying to keep a hard spec simple. Fact is, these specs might not even apply to most. They certainly don't have the force of law, but are often referenced in spec books, prints, and other contract documents. Just trying to help and generate discussion, is all.jpresort said:I would interpret 568: 4.4.2.4 to mean that you cannot have more than three outlets/jacks on a given cat5 cable rather than not more than three cat5's in a given conduit.
jpresort said:I definitely agree with the use of larger conduit or fewer cables than NEC would allow. How many of us have referenced Table C1 to see that it's acceptable to pull nine #12-thhn's in a 1/2" EMT and only tried that one time?
That's why I think 1/2" pipe has very little value, except for short runs to something in particular, like a single piece of utilization equipment, single receptacle, or a switch.Davis9 said:Hey, were you watching me?![]()
Tom:smile:
mdshunk said:That's why I think 1/2" pipe has very little value, except for short runs to something in particular, like a single piece of utilization equipment, single receptacle, or a switch.
Be carefull with "low voltage" thats not a code term at all.Shockedby277v said:Also does phone lines need to be seperated from other low voltage cables?
hbiss said:For your Cat5, the TIA-EIA 568 and 569 requirements...
Anything from the TIA-EIA are NOT requirements, they are just their recommendations, biased at best, and do NOT carry any regulatory weight. Most people ignore them unless you are a IT person or a member of BICSI who love to paste those "requirements" into job specs.
I don't want anyone to get the wrong idea and think I'm a BICSI nazi. Just trying to spice up what could be a boring conduit fill thread.mdshunk said:Fact is, these specs might not even apply to most. They certainly don't have the force of law, but are often referenced in spec books, prints, and other contract documents. Just trying to help and generate discussion, is all.