Cat 6 supported in the ceiling.

Status
Not open for further replies.

JdoubleU

Senior Member
Our low voltage cru is cutting into a hard lid cieling and is going to some mount access points for data. There will be an access hatch to get to those points. According to the NEC what and where does it talk about supporting the cables pulled to the access points. I would think that the Cat 6 cable would only need to supported where you can reach it from the access hatch and the rest of the cable could rest on the ceiling. I don't think you are required to take down the hard lid cieling to support the full length of the cable. Can anyone help me with this?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Take a look at 800.24.

800.24 Mechanical Execution of Work. Communications
circuits and equipment shall be installed in a neat and
workmanlike manner. Cables installed exposed on the surface
of ceilings and sidewalls shall be supported by the
building structure in such a manner that the cable will not
be damaged by normal building use. Such cables shall be
secured by hardware, including straps, staples, cable ties,
hangers, or similar fittings designed and installed so as not
to damage the cable. The installation shall also conform to
300.4(D) and 300.11.

Chris
 

JdoubleU

Senior Member
The wire will be above the ceiling not exposed. Does it have to be supported. If so we have to cutt into the hard lid ceiling to support the cable.
 