• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

cat5e ran vertcally in elevator shaft

Status
Not open for further replies.
I am running cat5e from our first floor to the roof for a wireless access point. The easiest way is though the elevator shaft. Does it have to be in emt? Does it have to be plenum rated?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This is not an NEC issue and in most cases nothing other than elevator associated piping, machinery, equipment, etc... is allowed in an elevator shaft or machine room, see ANSI 17.1 I believe.

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Roger, wouldn't 620.37(A) prohibit this install also?
I don't think so...the Cat 5 is a Chapter 8 installation...Chapter 8 is stand alone and 620.37(A) does not apply unless it says so in Chapter 8.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
don_resqcapt19 said:
I don't think so...the Cat 5 is a Chapter 8 installation...Chapter 8 is stand alone and 620.37(A) does not apply unless it says so in Chapter 8.
Don

Sorry Chris, I have to go with Don now. (I'm practicing being a politician:grin:)
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
don_resqcapt19 said:
I don't think so...the Cat 5 is a Chapter 8 installation...Chapter 8 is stand alone and 620.37(A) does not apply unless it says so in Chapter 8.
Don

Don, you and Roger are both killing me here. I have given up the 300.5 vs 725.3 argument. But chapter 8 is stand alone. Great.
Now show me something that allows Chapter 8 in my hoistway unless it is used directly in connection with the elevator.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Chris, that's where ASME A17.1 (elevator code) will come in.

Roger
 
Status
Not open for further replies.
Top