rf1031 said:
Do I have to run test lead all the way from fourth floor to ground rod? Since it is new york city and all electrical wiring is BX, could I just check for voltage to j-box or third pin of the closet receptacle? Electrician claims to have already checked resistance of ground and it was unmeasurable zero. So wouldn't anything I might find at ground rod also be present at closet grounds?
I don't own ammeter. Is voltage measurement enough to find problem (even if I can't find out how much current is there)? Can current be present without measurable voltage?
My reason for suggesting checking between the local problem (the coax shield in this case) and a remote real ground (the electrode, for example) is that the local ground (the nearest receptacle's EGC) would likely be at the same potential as other supposedly-grounded items (coax shield, for example).
In other words, you're using the local 'mesh' of wiring, appliances, plumbing, etc. around you on the third floor as your reference. The overheating conductive path, the coax, is connected between the local ground reference and the 'rest-of-the-world' ground reference. ("Welcome, Neo, to the real world.") Something is energizing one end of this conductive pathway.
There is a potential between the local ground (3rd floor) and the remote ground (real world) that is causing a current to flow on the coax shield. A clamp-on ammeter on the coax while it's being heated would show this current. Opening this pathway and measuring the voltage across the opening would show why.
Normally, the system neutral and/or EGC prevent this voltage by proper bonding. When this kind of problem exists, most of us reach the same initial conclusion: open neutral. Any conductor must present a low impedance for it to carry the current it should, and not allow an appreciable voltage difference between its ends.
Even the most complex of unusual problems obey Ohm's Law. Troubleshooting is all about applying the basics to the situation. You need to be able to note the symptoms, determine all of the possible causes, and then eliminate them, in groups first if possible, and then the remainders one at a time. Experience is paramount.
When you check for voltage on one wire that should be grounded, as compared to another wire that should be grounded, all you're proving is that the two are well bonded together. Your local shield is at the same potential as your local EGC. But, your incoming coax is melting. The other end is bonded to the real world, the earth.
With a properly-wired feeder, the EGC does not carry current, so should not present a voltage drop, which is why I suggest checking for voltages where there should not be any. Eliminate a group of suspects. So, if the local EGC is hot (re: the real world), one likely location of an open is ahead of the service (the utility side).
Of course, this is a jump of a conclusion, but it's a place to start.