catv installation for hospital patient rooms

Status
Not open for further replies.

abryf57

Member
I have been put in charge of installing new 24 volt televisions in the hospital where I work. I have a question about the cable installation process. Does the cable have to be in conduit where it drops down the headwall to the tv mounting plate. Thanks
 
Re: catv installation for hospital patient rooms

It does not have to be in concuit but if not, it would be a poor job. Use some type of surface raceway. You many be able to use non metallic depending on fire codes...
 