Probably. That situation is "opposite" of the way it would usually go, but still valid. Here is one list of series ratings
http://www.cooperindustries.com/con...ducation/solution-center/series_ratings0.html
What they said.I agree kind of the opposite of the way one usually looks at series ratings. If you had RK-5 fuses upstream, you probably wouldn't shell out extra $$$ for 65 kA breakers to be located downstream. I think most "standard interrupt rating" breakers will be series rated for use with RK-5 fuses. Most all that I have encountered in Square D certainly are.
The important thing to remember about series listings is that what you THINK is irrelevant. The only thing that counts is what the manufacturer has documented.
But if you had 65kA available and 65kAIC rated breakers, you would not need RK5 fuses ahead of them. But you MIGHT be able to use 25kAIC breakers by having RK5 fuses ahead of them, and that could save significant coin. Likewise if you have 90kA available, you can possibly use 65 kAIC rated breakers + upstream fuses. But ALWAYS remember to RTFM.
As to someone constantly replacing fuses and closing into the same fault, I’ve seen people do that with breakers too, until they weld the contacts or blow. Nothing is idiot proof, the universe just keeps making better idiots.