Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Seems like boiler plate garbage. #10 solid for more than 3 CCC's? Where do they get this stuff?
Serious question not rhetorical: So who do you think actually comes up with all this masterbatory stuff? I would guess it's typically some engineering firm?The people who write this stuff have never turned a single wire nut in their entire lives. They have to write SOMETHING, or else they'd be out of a job.
Probably a lawyer.Serious question not rhetorical: So who do you think actually comes up with all this masterbatory stuff? I would guess it's typically some engineering firm?
Assuming these notes are specifically for 20A branch circuits, this seems like a note from an engineer/designer who is unaware that you may derate from the 90 degree column when using THHN/THWN-2. The derating math works out for a 20A branch circuit if there is a 20A limitation for #12s and a 30A limitation for #10s instead of 30A/40A respectively.Serious question not rhetorical: So who do you think actually comes up with all this masterbatory stuff? I would guess it's typically some engineering firm?
I agree but I do think they assumke most homeruns will have more than #9 CCC so #10's would be correct for 20A circuit.Seems like boiler plate garbage. #10 solid for more than 3 CCC's? Where do they get this stuff?
But if you're assuming more than 9 why say more than 3? Some of these designs are a tremendous waste of money.I agree but I do think they assumke most homeruns will have more than #9 CCC so #10's would be correct for 20A circuit.
It's like a software interface designed by someone who never has to use it.The people who write this stuff have never turned a single wire nut in their entire lives. They have to write SOMETHING, or else they'd be out of a job.
Don't hate me... I don't agree entirely how the note is written, but we find that on many job sites ECs will pack a 2" conduit longer than 24" with conductors and think its okay. I don't agree that they should be limiting the contractor to #10s for 4 or more conductors... but some responsibility has to be taken into account for the EC knowing the codes and not accounting for the adjustment factor on their builds.
Seems like boiler plate garbage. #10 solid for more than 3 CCC's? Where do they get this stuff?
Would you guys actually follow that note about no more than 9 ccc's in raceway?Sure contractors do all sorts of dumb things but that why you need to have someone checking their work before they get paid. The nonsense in the OP is a colossal waste of someone's money.
If your contract has a clause for value engineering then you can suggest not following those requirements and install per code to save money. If you're installing separate neutrals how stupid is it to only have 4 circuits in a raceway.Would you guys actually follow that note about no more than 9 ccc's in raceway?
Why would separate neutrals matter in regards to circuit qty? I know there more wires but don't understand your pointIf your contract has a clause for value engineering then you can suggest not following those requirements and install per code to save money. If you're installing separate neutrals how stupid is it to only have 4 circuits in a raceway.
You stated no more than 9 CCC's in any raceway. If you have (4) 2-wire circuits that's 8 CCC or the maximum of 4 circuits. If you pull (5) 2-wire circuits that's 10 CCC's and you've exceeded their magic number of 9.Why would separate neutrals matter in regards to circuit qty? I know there more wires but don't understand your point
That is a code requirement in the Chicago Electrical Code. No idea if it is in the NYC code.Would you guys actually follow that note about no more than 9 ccc's in raceway?
It's not in the NYC electrical code.That is a code requirement in the Chicago Electrical Code. No idea if it is in the NYC code.