Pertaining to 1P-20A receptacle circuits and derating per 310.15 (C) (1) would you count the neutral as current carrying?
YesPertaining to 1P-20A receptacle circuits and derating per 310.15 (C) (1) would you count the neutral as current carrying?
Unless it's a shared conductor that only carries unbalance current, yes.Pertaining to 1P-20A receptacle circuits and derating per 310.15 (C) (1) would you count the neutral as current carrying?
Since you said "circuits" plural, but "the neutral" singular, then you may be considering an MWBC. In which case a 3-wire 120/240V MWBC is only 2 CCCs, and a 4-wire 208/120Y MWBC is only 3 CCCs.Pertaining to 1P-20A receptacle circuits and derating per 310.15 (C) (1) would you count the neutral as current carrying?