ivsenroute
Senior Member
- Location
- Florida
I am having a difference of opinion that I would like to have clarified or debated here.
I think the following is acceptable.
A 20' piece of proper rebar (5/8" bare steel) is being used as a CEE. The last 18" come out the top of the footer and will be bent downward and encased in concrete when the basement floor is poured. The electrical inspector was present for the footing pour to verify the proper installation of the rebar.
A properly sized GEC is attached to the end of the rebar in question with a clamp that is listed and labeled for attachment to rebar and for both DB and concrete encasement.
Would this be a compliant installation?
I think the following is acceptable.
A 20' piece of proper rebar (5/8" bare steel) is being used as a CEE. The last 18" come out the top of the footer and will be bent downward and encased in concrete when the basement floor is poured. The electrical inspector was present for the footing pour to verify the proper installation of the rebar.
A properly sized GEC is attached to the end of the rebar in question with a clamp that is listed and labeled for attachment to rebar and for both DB and concrete encasement.
Would this be a compliant installation?