iwire Moderator Staff member Location Massachusetts Feb 9, 2009 #21 cowboyjwc said: According to 250.52(A)(3) you can bond the rebar with the tie wire, but it doesn't say anything about splicing the electrode. Click to expand... That is the same thing IMO.:-?
cowboyjwc said: According to 250.52(A)(3) you can bond the rebar with the tie wire, but it doesn't say anything about splicing the electrode. Click to expand... That is the same thing IMO.:-?
M. D. Senior Member Feb 9, 2009 #22 I managed to become confused,. what are we talking about.. I also wonder at the use of the word or in the the code section as in 20' vert. or 20' horz. Can it be both H & V for a combined measurement ? as in 6' H then bend up for 14' ???
I managed to become confused,. what are we talking about.. I also wonder at the use of the word or in the the code section as in 20' vert. or 20' horz. Can it be both H & V for a combined measurement ? as in 6' H then bend up for 14' ???
cowboyjwc Moderator Staff member Location Simi Valley, CA Feb 9, 2009 #23 iwire said: That is the same thing IMO.:-? Click to expand... I didn't say I wasn't splitting hairs.
R raypoud Member Feb 11, 2009 #24 Is 20' of rebar ("within and near the bottom") the same concept of 8' ("below permanent moisture level") of a rod?
Is 20' of rebar ("within and near the bottom") the same concept of 8' ("below permanent moisture level") of a rod?