What is section that i need to enforce? If the wire type CEE is used it has to be continuous to the panel. unless irreversible splices are made.
First you need to determine if there are other grounding electrodes present, if there is only one of them needs to be connected to the unspliced grounding electrode conductor, the others can be (don't have to be) connected via bonding jumpers.
If your CEE is the only grounding electrode then the GEC will run to your only electrode and there are no bonding jumpers to other electrodes.
250.64(C) is the section that says GEC must be continuous.
250.50 mentions that all electrodes present (and describes what is an electrode via other sections) must be bonded together to form the "grounding electrode system"
250.53(C) mentions the bonding jumpers.
No where does it specifically say you must run a GEC to each electrode, it only says you must have a grounding electrode conductor, and that you can use bonding jumpers to tie electrodes together to form a grounding electrode system.
This usually means you will run a full size GEC to water pipe electrodes or building steel electrodes if present and can run reduced sized conductors as permitted to rods, pipes, plates, CEE's. Those smaller permitted conductors are typically what is connected via bonding jumper to the full sized GEC when it is done that way.