SAP

Senior Member
Location
Fresno Ca
I'm doing a residential service change no uffer no ground rods, It has a existing # 4 solid going straight into the concrete it is visible I can see it . from my experience we really only see that kind of GEC in commercial application. The Inspecter faild me . I want to get some input before I call his supervisor thanks
 
The NEC describes what CEE is made of and how it is constructed.

The inspector cannot see through the concrete so they cannot verify it is a qualifying electrode.

In my opinion the inspector is within their authority to require a grounding electrode they can verify.
 
The copper I'm sure runs 20 feet in the footing, he can see we're it enters the concrete, just like connecting to rebar with ground clamp, Inspecter can't see we're the rebar goes after enters concrete, thanks for the input
 
The copper I'm sure runs 20 feet in the footing, he can see we're it enters the concrete, just like connecting to rebar with ground clamp, Inspecter can't see we're the rebar goes after enters concrete, thanks for the input

The ufer normally gets inspected prior to the footing being poured so they do see the 20' of copper or rebar. You could ask the building department if they can and are willing to access previous inspection records to confirm the Ufer was signed off. The only other option is to add rods and move on.
 
So we have gone from mandating that a cce be used when present because it is a far better grounding electrode than a ground rod to replacing an existing cce with a ground rod? I don't see the sense in it. Hold your ear close to your screen and you might be able to here the sound of me banging my head on my desk.
 
Isn't there a way to test the existing CEE?

IMO there is no current technology that can verify the current NEC CCE requirements.

The NEC would have to add a perimeter say 25 ohms but substantiating any number might be hard.

When does an electrode become 'good enough'?
 
So we have gone from mandating that a cce be used when present because it is a far better grounding electrode than a ground rod to replacing an existing cce with a ground rod? I don't see the sense in it. Hold your ear close to your screen and you might be able to here the sound of me banging my head on my desk.

I can understand that thought and I appreciate the logic in it.

But if we can't see the CCE and there are no records of it being inspected before what is the logical thing to do?
 
I can understand that thought and I appreciate the logic in it.

But if we can't see the CCE and there are no records of it being inspected before what is the logical thing to do?
I don't understand people's fascination with grounding electrodes any more than I understand a woman's reaction to a bouquet of roses, especially a ground rod.

The logical thing for me, knowing that half good cce is better than a pair of ground rods any day of the week, would be to inspect the connection to it and be happy.
 
I don't understand people's fascination with grounding electrodes any more than I understand a woman's reaction to a bouquet of roses, especially a ground rod.

Amen brother ... :lol::lol:

But if you were an inspector and you had to approve a mystery wire how can you do that?

The logical thing for me, knowing that half good cce is better than a pair of ground rods any day of the week, would be to inspect the connection to it and be happy.

How do you know it is a CCE?
 
I agree if the CEE can't be verified somehow, the next step would be to establish the next best thing, water pipe or two rods. But, I would still connect the CEE to the grounding system along with the other electrcodes. Is there a reason that one wouldn't want to do that? I can't think of one.
 
I agree if the CEE can't be verified somehow, the next step would be to establish the next best thing, water pipe or two rods. But, I would still connect the CEE to the grounding system along with the other electrcodes. Is there a reason that one wouldn't want to do that? I can't think of one.

:slaphead:
I worded this poorly. What I meant was to establish the water pipe or, if no water pipe is available, two rods as the primary electrode. The water pipe would obviously be used already, but as a secondary to the CEE.
 
How do you know it is a CCE?

Of course I would have no way to be 100% sure without major surgery, but I would willing to take some educated guesses based on the building's age, check past permits and type of work that was done prior to most recent inspection, yada yada yada. If there was some foundation work done post '05 and I saw a piece of #4 copper sticking out I would feel just fine about it being a gec.
 
Ditto what iwire said. Pound in 2 rods and move on, not worth trying to argue.

Be careful where you put those two rods. Best to miss the underground feeders, gas lines, and water lines. I know a call to 811 takes too long. I always cross my fingers and wince a bit while pounding.
 
When I go to a service change, I look for the GEC if it looks like there is a CEE but there is no access to it ( blank cover) I pull my service out look down the cavity and 9 times out of ten I can see the rebar and ground clamp I cut me a hole were the ground clamp is , put a 2 gang low voltage cut out box with a bell box cover. Now it is accessible. That's what I did today but instead of rebar going into the concrete it was bare # 4, if you take off blank cover you can clearly see it going into the concrete. I ended up getting it passed, I guess they are used to seeing ground rods, I find for me that it is easier to drive one ground rod right under the panel, then to try to locate the existing CEE, but most AHJ want you to drive 2 that's when it becomes a headache for me, I do whatever is easiest at the time
 
When I go to a service change, I look for the GEC if it looks like there is a CEE but there is no access to it ( blank cover) I pull my service out look down the cavity and 9 times out of ten I can see the rebar and ground clamp I cut me a hole were the ground clamp is , put a 2 gang low voltage cut out box with a bell box cover. Now it is accessible....

You shouldn't have to do that, 250.68(A) already requires the rebar connection above grade to be accessible.
 
Of course I would have no way to be 100% sure without major surgery, but I would willing to take some educated guesses based on the building's age, check past permits and type of work that was done prior to most recent inspection, yada yada yada. If there was some foundation work done post '05 and I saw a piece of #4 copper sticking out I would feel just fine about it being a gec.

And I agree an inspector could do that.

At the same time I cannot fault an inspector for not doing that. So this brings me back to my original response. IMO the inspector can require a verifiable electrode.
 
And I agree an inspector could do that.

At the same time I cannot fault an inspector for not doing that. So this brings me back to my original response. IMO the inspector can require a verifiable electrode.
And since when have ground rods been verifiable?
Does the inspector measure the length, put a stamp on the rod, and then verify the stamp once it has been driven?
How does he know you did not cut five feet off the end?