Besides for the code specified locations for UL rated fan boxes in a ceiling ie. bedrooms, kitchens, yada yada. Is it permisable to use 1900 boxes in the remainder of the locations ie. hallways, and closets?
The NEC only requires a fan rated box where a fan is directly supported from the box. "Sole Support"By Peter: I'm not aware of an NEC requirement but I still think it's a good idea to install fan boxes in all locations but closets and hallways.
We don't use the box as the sole means of support as we run long screws into the truss or made structural member behind the box.314.27(D) Boxes at Ceiling-Suspended (Paddle) Fan Outlets. Where a box is used as the sole support of a ceiling-suspended (paddle) fan, the box shall be listed for the application and for the weight of the fan to be supported. The installation shall comply with 422.18.
You don't have to use fan boxes anywhere unless you are planning to install a fan.Originally posted by chicago_sparky:
Besides for the code specified locations for UL rated fan boxes in a ceiling ie. bedrooms, kitchens, yada yada. Is it permisable to use 1900 boxes in the remainder of the locations ie. hallways, and closets?
Yes, I know that. I was talking about a requirement to install them in places that a fan is likely to be installed, like a bedroom. As Scott said, that requirement doesn't exsist.Originally posted by hurk27:
The NEC only requires a fan rated box where a fan is directly supported from the box. "Sole Support"
Allen, read more carefully. The CEC. (Chicago Electric Code)Originally posted by allenwayne:
What article are they using[
Originally posted by peter d:
Originally posted by allenwayne:
What article are they using![]()