tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Interesting and sad you have to double check on eng. EE plans mostly are not that great, it’s $ per sheet. You saved someone from a change order
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Here is one for Eaton CH breakers, I imagine all manufacturers have something similar. Square D has gangable ones too for the QO style.
 

Attachments

  • E5FE5B6B-7C40-4C1D-AA1B-CA2DCB167B59.png
    E5FE5B6B-7C40-4C1D-AA1B-CA2DCB167B59.png
    311.3 KB · Views: 9

MyCleveland

Senior Member
Location
Cleveland, Ohio
Exactly, and usually the fourth circuit is from a different isolated ground panel or fed from a UPS/UPC panel.
I have seem this also numerous times and always thought it was a violation.
Forgive the highjack…”hh”.

Source 1: 3h-n-g
Source 2: h-n-IG
Don’t say you could bring a third g wire from source 2, because the factory whips have 8 wires.

If Source 2 plug hot wire faults to case…does circuit clear ?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I have seem this also numerous times and always thought it was a violation.
Forgive the highjack…”hh”.

Source 1: 3h-n-g
Source 2: h-n-IG
Don’t say you could bring a third g wire from source 2, because the factory whips have 8 wires.

If Source 2 plug hot wire faults to case…does circuit clear ?
The isolated ground is still a ground common to the other ground, it just does not rely on the conduit as a return path. If properly installed, both panel grounds are bonded. I have seen many times, the isolated ground incorrectly installed, and truly insulated back at the panel.
 