I just want to make sure I'm going about this the right way. I'm trying to determine minimum service size.
I've calculated and distributed the volt-amps for each of the loads shown in the attachment. A-phase carries the largest load, so I'm going to use that for my calculations.
My problem is, if I calculate out amps for each load and fill out the panel schedule I get 510 amps on A phase.
I can't figure out how to get 510 amps using the VA values listed in my drawing to calculate amps.
If I separate out the 120 v loads (first 5 loads) and calculate amps from those I get 39,221.8va/120v = 326.8 A
The total VA for the 3-ph loads add up to 25,395.7va. In order to get a total of 510 amps, I have to divide the 25kva by 138v which doesn't make sense to me. (138 v = 240/1.732)
I've calculated and distributed the volt-amps for each of the loads shown in the attachment. A-phase carries the largest load, so I'm going to use that for my calculations.
My problem is, if I calculate out amps for each load and fill out the panel schedule I get 510 amps on A phase.
I can't figure out how to get 510 amps using the VA values listed in my drawing to calculate amps.
If I separate out the 120 v loads (first 5 loads) and calculate amps from those I get 39,221.8va/120v = 326.8 A
The total VA for the 3-ph loads add up to 25,395.7va. In order to get a total of 510 amps, I have to divide the 25kva by 138v which doesn't make sense to me. (138 v = 240/1.732)