I don't think they would argue that it would shock you. They would argue that they got shocked by Vnb NOT Vbn.
Either way, it still hurts.
I don't think they would argue that it would shock you. They would argue that they got shocked by Vnb NOT Vbn.
Been there, done that, never considered the polarity.[/B]
Either way, it still hurts.![]()
I was thinking about hooking these up and getting some scope shots then thought better of it.111109-1758 EST
jjkind:
To make it simple consider a single air core coil.
If I apply a steady DC input, then B is a constant value.
If the input is a pulsating DC (never negative), then B never changes sign.
If the input is a balanced AC, then B is a balanced +/-B.
Next add a second coil magnetically coupled by air to the first coil. There is no DC coupling.
For the steady DC input there will be a short pulse output from the secondary at the transistion of the input. After steady-state the output is 0.
For the unidirectional pulsating DC after steady state the secondary is an AC voltage with an avetrage value of 0. Meaning the areas above and below 0 are equal.
The third case is the same result except that the voltage waveform is balanced.
.
Been there, done that, never considered the polarity.
The worst is learning that the neutral is a conductor. It ain't neutral at all: it takes sides, and it ain't yours.![]()
However, I was curious about the impact of feeding a DC signal, like a rectified 5-10 volt AC into the primary side of a 120:30 transformer I have laying around my workbench somewhere. I would not anticipate any damage, but then am I left to demagnetize it? I don't ever recall purposely feeding a DC signal into a transformer and have not given it much thought other than knowing that it is not what we want to do and can saturate the transformer (ignoring ferroresonant transformers for the moment).
Pardon my flippancy, but I can't help but make the observation. This discussion is kind of like going to the dance at an all-boys school. Has it not occurred to you guys that you are all standing alone on one side of the room?
:jawdrop:
You've been carrying on an argument for 30 postings, and none of you have noticed that the other side isn't even participating? :lol::lol::lol:
I'm sorry. Please carry on with what you were saying. :angel:
Let's say each winding turn adds 1 volt per turn. The secondary winding has 120 turns and 120 volts out. Starting from the winding end, which is either L1 or L2 the winding turns add 1 volt out each in series to the winding center, system grounded point, which yields 120 volt.
As I contiue adding winding turns past the neutral point, what happens. The winding turns continue adding identically in phase, in series. Output voltage progresses 121 volt, 122, 123 volt ..
If the subsequent winding turns past the neutral point were "180 out of phase" each added turn, the output voltage would go 119 volt, 118, 117 .. In fact, this paradigm fails this test.
Some part of your audience wants to know "what happens" and you have the O O P repeating gobbledegook 240 is "the voltage are 180 out of phase" when he could have been saying, the "the wiindings are in series (and matched)". It makes my ears hurt.
111111-2334 EST
rattus:
What was your connection with the Signal Corp?
.
Let's say each winding turn adds 1 volt per turn. The secondary winding has 120 turns and 120 volts out. Starting from the winding end, which is either L1 or L2 the winding turns add 1 volt out each in series to the winding center, system grounded point, which yields 120 volt.
As I contiue adding winding turns past the neutral point, what happens. The winding turns continue adding identically in phase, in series. Output voltage progresses 121 volt, 122, 123 volt ..
If the subsequent winding turns past the neutral point were "180 out of phase" each added turn, the output voltage would go 119 volt, 118, 117 .. In fact, this paradigm fails this test.
Some part of your audience wants to know "what happens" and you have the O O P repeating gobbledegook 240 is "the voltage are 180 out of phase" when he could have been saying, the "the wiindings are in series (and matched)". It makes my ears hurt.
The proper way to do this is to start at neutral when you are adding turns. Then for L1 say, you are adding 1V at 0 until you reach 120V.
But when adding turns between N and L2, the sense of the windings is reversed, so you are adding 1V @ 180 with each turn.
This is the whole idea of establishing a reference point.
Got it?
You are making my point for me. The description leads to confusion.
The winding does not start at the neutral. It starts at an end, L1 or L2. This is the physical reality of the device as fabricated by the manufacturer. The neutral is at the middle of the winding and the physical turn direction continues homogeneous. The fact of the winding does not reverse.
Reversal comes as an artifact of how the meter leads or loads are attached to the sources. The leads reverse after the output, between the source and the load. Winding turn direction does not reverse.