Does addition of a natural gas line in the process area change the area classification from non-classified to Class 1 hazardous?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Not necessarily. See Section 500.5(B)(2) IN No.2. : Piping without valves, checks, meters, and similar devices would not ordinarily introduce a hazardous condition even if used for flammable liquids or gases.

The converse is not necessarily true; I.e.,Piping with valves, checks, meters, and similar devices will not necessarily create a classified location either - but the analysis is far more stringent.
 

Markmy

Member
Location
NJ
Occupation
Engineer
.Thank you for pointing to the NEC. Yes, I believe that even in case of bad pipe leak, the concentration of flamable gases in the air is in insufficient quantity to become explosive or ignitable.