Can't do it.
Install an isolation transformer 480-480/277V and a downstream 480/277V panelboard.
We don't know what we don't know.Ron not sure I agree. Sounds like there is a 480/277 supply, just the panelboard is marked 3 wire. Now if the OP is talking about stealing a neutral from another system then i agree no.
the MSB is 277/480V. E.C. is going to check to see what wiring is actually pulled. may have to install a 480D to 277/480 xfmr and panelboard
If you have 480/277v available already I don't see why you'd have to install a transformer.