al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
This is a question based on the 2014 NEC. What will your local electrical inspector, under the 2014 NEC, say about the scenario below?
I work in an area that has a lot of "all-metal wiring methods" in existing homes built after WWII. A common hookup for a residential disposal is to have a 1/2" flexible metallic conduit running from an above counter backsplash mounted switch down into the undersink cabinet where the 1/2" flex directly connects to the disposal.
I have a situation where an air switch is desired to be mounted on the back sink top, beside an instant Cup-O-Soup hot water dispenser. Both the hot water dispenser and the disposal will share the 15 Amp 120 Volt branch circuit formerly dedicated only to the disposal. For those who haven't seen it, there are two receptacles on the air switch module, one for the disposal and one for the hot water dispenser, and only one can be energized at a time. Given how briefly most disposal operation is, this works out just fine in normal residential use. Both Disposal and Hot Water Dispenser are cord and plug connected.
The problem is the hardwired 1/2" flex whip gets altered into a surface mounted receptacle for the air switch module to plug into, thus invoking the 2014 NEC requirements for both GFCI and AFCI protection at the new receptacle outlet.
In strapping down the 1/2" flex, shortening it a little, and adding a surface mounted junction box with a two gang raised metal cover, I can connect the flex whip conductors to the LINE terminals of a blank face GFCI device, and, in turn, connect the LOAD side of the GFCI to the LINE side of an Outlet Branch Circuit AFCI device.
Only the disposal and the Cup-O-Soup hot water dispenser are being installed. There is no remodel or open walls. This seems to be the minimum 2014 NEC compliant solution.
What would your local authority having jurisdiction say?
I work in an area that has a lot of "all-metal wiring methods" in existing homes built after WWII. A common hookup for a residential disposal is to have a 1/2" flexible metallic conduit running from an above counter backsplash mounted switch down into the undersink cabinet where the 1/2" flex directly connects to the disposal.
I have a situation where an air switch is desired to be mounted on the back sink top, beside an instant Cup-O-Soup hot water dispenser. Both the hot water dispenser and the disposal will share the 15 Amp 120 Volt branch circuit formerly dedicated only to the disposal. For those who haven't seen it, there are two receptacles on the air switch module, one for the disposal and one for the hot water dispenser, and only one can be energized at a time. Given how briefly most disposal operation is, this works out just fine in normal residential use. Both Disposal and Hot Water Dispenser are cord and plug connected.
The problem is the hardwired 1/2" flex whip gets altered into a surface mounted receptacle for the air switch module to plug into, thus invoking the 2014 NEC requirements for both GFCI and AFCI protection at the new receptacle outlet.
In strapping down the 1/2" flex, shortening it a little, and adding a surface mounted junction box with a two gang raised metal cover, I can connect the flex whip conductors to the LINE terminals of a blank face GFCI device, and, in turn, connect the LOAD side of the GFCI to the LINE side of an Outlet Branch Circuit AFCI device.
Only the disposal and the Cup-O-Soup hot water dispenser are being installed. There is no remodel or open walls. This seems to be the minimum 2014 NEC compliant solution.
What would your local authority having jurisdiction say?