Thank you for that.If all you are doing is adding that insta-hot, my local AHJ is not even getting contacted as there is no requirement to even file for a permit on this job.
Will I install additional GFCI or AFCI in that situation? Will have to wait until that job comes up to find out I guess, but the GFCI is a possibility, the AFCI is probably not happening if no one is forcing it, but that is a whole other thread.
Look, the OP is not asking about "insta-hot water dispensers". I'm asking about dealing with a hard wired outlet at the end of a dedicated 120 V residential disposal circuit, with no other outlets, that is one side of a multiwire branch circuit homerun. I am not adding a NEW outlet. I'm modifying an existing outlet from hardwired outlet to receptacle outlet.
When the hard wired outlet (wirenut splice) is modified to a receptacle outlet, the current NEC in effect is invoked. Regardless of whether I pull a permit, or not, my OP question is about what will be accepted by local inspection as Code compliant. . .
When the 2014 NEC is the Code in effect, modifying an existing residential disposal hard wired outlet to a receptacle outlet involves 210.8, 210.12, 406.4, 406.12 and probably a couple more. But these are the main ones.
The modified receptacle outlet is the first outlet on the existing branch circuit . . .