Thanks Dennis, what I wanted to know is what is a combination connector ?
Got a mixture of terminologies flying around here. Eaton/Cooper/Crouse-Hinds calls them combination couplings.Thanks Dennis, what I wanted to know is what is a combination connector ?
No. To use it with MC it must be listed for use with MC... though there are many electricians out there that completely disregard the listing or know no better and use an FMC coupling or connector anyway.So when a combination connector says EMT to FMC that also includes MC ? that is what i would like to know, what is considered FMC ?
So you are saying you're going to strip the MC except this short section to make the total length of conductors?Found a Bridgeport 280-DCX online, Says its listed for MC. Now to find it locally.
Incompatibility of the thread has little to do with it. It's simply a matter of listing compatibility. Consider the fact we use tapered thread mated with straight thread all the time with rigid or IMC conduit and standard couplings... but the tapered thread is always on the conduit and the straight thread is always on the coupling, the female side of the joint.
How long is the run on each end of the MC section?Roger, I may do that yes.Do you see an issue with doing it that way ?
That's not to bad then, I thought you might be talking a pretty long distance.Roger the stripped out MC would be around 10 feet.
So my supply house has the Bridgeport 280 DC, the 280 DCX is listed for MC. The DC is listed for Flex? and even NM. I've never used FMC, do we just add our stranded THWN and treat it like MC? does it require antishort bushing?