I just re-read Note 7 and I am perplexed by it. It seems to say that you round up when the calculation is .8 or greater rather than .5, however it also states this applies only when the conductors are all the same size. Therefore, I could not round up at all if I had different size conductors. Why would that be true?
When calculating the maximum number of conductors
or cables permitted in a conduit or tubing, all of the
same size (total cross-sectional area including insulation),
the next higher whole number shall be used to
determine the maximum number of conductors permitted
when the calculation results in a decimal greater
than or equal to 0.8. When calculating the size for
conduit or tubing permitted for a single conductor, one
conductor shall be permitted when the calculation
results in a decimal greater than or equal to 0.8.