brycenesbitt
Senior Member
- Location
- United States
What relevant concerns would you see with this odd, but, seemingly safe sketch design?

Currents are not a problem, as anything used by the new subpanel will either reduce the current through the main panel breaker, or just
reverse the current flow.
CEC Section 705.12 and NEC Section 690-64(b)(1) wants a "dedicated" circuit for the solar. Is the demarcation point the disconnect or the main panel?
In other words could the dedicated circuit be defined to start at the right half of the diagram, downstream of the mechanical disconnect?

---------------------------------------------
The solar inverter has two disconnects both within sight of the unit: a 30A breaker at the main panel, and the above flip switch disconnect.
The wires are #8, with the neutral passing straight through the disconnect box. Total conduit length is about 10 feet from main to inverter.
The main panel has only two conduits that transit through a stucco wall. The goal is to share one of those two conduits
to avoid the hassle of a third penetration. While breakers could be added to the old subpanel, it's a terrible icky Federal Pacific model.
See also
---------------------------------------------
Is there a conduit fill table for mixed wire sizes, e.g. four #8s plus 4 #12's?
Is four #8's plus four #12's acceptable in the left half conduit?

Currents are not a problem, as anything used by the new subpanel will either reduce the current through the main panel breaker, or just
reverse the current flow.
CEC Section 705.12 and NEC Section 690-64(b)(1) wants a "dedicated" circuit for the solar. Is the demarcation point the disconnect or the main panel?
In other words could the dedicated circuit be defined to start at the right half of the diagram, downstream of the mechanical disconnect?

---------------------------------------------
The solar inverter has two disconnects both within sight of the unit: a 30A breaker at the main panel, and the above flip switch disconnect.
The wires are #8, with the neutral passing straight through the disconnect box. Total conduit length is about 10 feet from main to inverter.
The main panel has only two conduits that transit through a stucco wall. The goal is to share one of those two conduits
to avoid the hassle of a third penetration. While breakers could be added to the old subpanel, it's a terrible icky Federal Pacific model.
See also
Chase branch circuits through main disconnect.
Yes, it doesn't need a drip loop, The problem is that I don't have enough slack in the service cable to cut it, put a new meter in and splice it. They make new conductor;) You probably only needing 10-20 foot lengths not a 1000' reel.
forums.mikeholt.com
---------------------------------------------
Is there a conduit fill table for mixed wire sizes, e.g. four #8s plus 4 #12's?
Is four #8's plus four #12's acceptable in the left half conduit?