Shaneyj
Senior Member
- Location
- Katy, Texas
- Occupation
- Project Engineer
My goal is to accurately size a vfd and a phase converter for single phase input (240v) and 3 phase output (480v).
If I understand correctly, the vfd needs to be sized at 1.73 (sq rt 3) times the rated voltage current. Is this correct?
My numbers...
Nameplate v: 480
Nameplate i: 31
480*31*1.73=25.8kVA= rated operating power
25.8kVA*1.73=44.6kVA= operating power on 230v vfd supply
44.6kVA/230= 193.9 A
Would I need a vfd rated at 193A?
Would deriving phase converter current be the same method as vfd?
This is for a plasma table.
Thanks for the input.
Sent from my HTC6545LVW using Tapatalk
If I understand correctly, the vfd needs to be sized at 1.73 (sq rt 3) times the rated voltage current. Is this correct?
My numbers...
Nameplate v: 480
Nameplate i: 31
480*31*1.73=25.8kVA= rated operating power
25.8kVA*1.73=44.6kVA= operating power on 230v vfd supply
44.6kVA/230= 193.9 A
Would I need a vfd rated at 193A?
Would deriving phase converter current be the same method as vfd?
This is for a plasma table.
Thanks for the input.
Sent from my HTC6545LVW using Tapatalk