The VFD rectifies incoming AC to DC then converts the output to a pulsed DC over three lines that approximates a three phase source. It is by no means perfect sinusoidal wave like would be from a generator, nor is is as perfect as an inverter from a UPS, PV, or other similar systems would produce.Not sure what you mean by "inverter".
I've got a single phase source and a 3 phase piece of equipment.
I thought a vfd or a phase converter were the only way to manufacture 3 phase from single phase.
On another note, why would a plasma cutter care about the incoming wave? Does it not condition the input and put out a modified wave?
Maybe a call to hypertherm is in order.
Sent from my HTC6545LVW using Tapatalk
That said, the plasma cutter may not have a problem with what a VFD will produce for output, but I can almost assure you the VFD will not like the plasma cutter connected to it's output. You turn drive on and get it up to 60 Hz and 460-480 volts and then suddenly switch some load on - it will see that like a short circuit and will trip if you are lucky. If not luck will burn out components. It is designed for ramping a motor up from low voltage and low frequency, not suddenly throwing a load onto it's output.
Some of the drive experts can explain the technicalities much better then I can.