josh greene said:Well i bet that's not legal, not even in n.c.
Why not ? I have installed similar with bell box for better looks.
josh greene said:Well i bet that's not legal, not even in n.c.
m73214 said:Give me the code reference citing the violation.
2005 NEC
314.27(C)
Floor Boxes
Boxes listed specifically for this application shall be used for receptacles located in the floor.
iwire said:On the floor is different then in the floor.
No violation.
How do you know? Got X-ray vision? That box might get busted up with a buffer, but I believe the receptacle will fare just fine.K8MHZ said:I don't see this box as complying with 406.8 (D) as the box is mounted on the floor without standpipes.
mdshunk said:How do you know? Got X-ray vision? That box might get busted up with a buffer, but I believe the receptacle will fare just fine.
A determined person can bust anything up.K8MHZ said:With receptacles that tough, who needs a box??
:grin:
mdshunk said:A determined person can bust anything up.