I was just wondering how you can check to see if a DC motor is bad. I know you can use a Megger on a 3 phase AC motor and other AC motors, but can you use a megger on DC? If not what do you use to check them? I am now working at a plant that uses a lot of DC motors, I am fairly new to these because my last job used mostly 3 ph 480v motors. Any help would be appreciated.

Thanks,
Jeremy
 
shunt or series?

edit: i think in either case a voltage drop test of AC across the field leads should all be equal. If you have an infrared tester, 140 degrees is normal top end in most cases for motor
 
Last edited:
You still do a IR test, if >150kW do a PI test, otherwise just a DAR.

Check bolted connections with DLRO.

High pot test per NEMA MG1, section 3.1

You can also do a voltage drop test as danickster mentioned but it is an optional test.

Your DAR/PI should be >1
Your IR at 40 degrees C should be >100M
 