I found a chart that I have that says "Troubleshooting" at the top then it says" Open-Circuit Voltage Test Limits"
Then it has all the ballasts types, ie:mercury, metal halide, HP Sodium, Low Pressure Sodium.
Within each ballast type there is Wattage - ANSI number - RMS Voltage
Now I don't remember why I have this or where I got it but is it for checking output on HID ballasts?
If so that's what I need.
Let's say you have a MH ballast (M59) and the lamp is 400W and the RMS voltage listed is 225-255, does that mean you should have that voltage output from the ballast?
I don't understand, if it means the output voltage wouldn't you also need the line voltage supplying the ballast to be in the chart? Example: if the line voltage was 277V, that's already higher than the 225-255V listed in the chart.
Also, where would you take the measurement from to test this? Would you first remove the lamp then check between the contact in the base and neutral/shell of the socket? Or better I suppose, test the leads to the socket?
I just need a way to determine if only the lamp needs replacing or the ballast kit, or both.
Then it has all the ballasts types, ie:mercury, metal halide, HP Sodium, Low Pressure Sodium.
Within each ballast type there is Wattage - ANSI number - RMS Voltage
Now I don't remember why I have this or where I got it but is it for checking output on HID ballasts?
If so that's what I need.
Let's say you have a MH ballast (M59) and the lamp is 400W and the RMS voltage listed is 225-255, does that mean you should have that voltage output from the ballast?
I don't understand, if it means the output voltage wouldn't you also need the line voltage supplying the ballast to be in the chart? Example: if the line voltage was 277V, that's already higher than the 225-255V listed in the chart.
Also, where would you take the measurement from to test this? Would you first remove the lamp then check between the contact in the base and neutral/shell of the socket? Or better I suppose, test the leads to the socket?
I just need a way to determine if only the lamp needs replacing or the ballast kit, or both.