knickelj
Member
- Location
- SE Wisconsin
I have 2 motor controllers, and have been assigned the task of adding 1 small chemical pump that would only be energized (cord and plug NEMA 5-15) when any one of the controllers is engaged. These are boiler feed water pumps and the chemical injector only should pump when the feed water pump is running. We have these set-ups in a bunch of our buildings but have not had to look into how they electrically fed the chem. pump. And from what I've seen I wouldn't trust copycatting anyway. Is there anything in the code that would prevent load side taps from the controller to a single receptacle to power the chem. pump. Seems like you should not be able to control a receptacle through a contactor??? For arguments sake lets assume all our other requirements are met (they will be) OCPD, cir ampacity etc. Both motor controllers are fed from the same branch circuit and tapped before the controllers. As an alternate, I know I could use aux contacts off of the controllers but they are not available (would have to replace both). And I thought of adding a separate contactor controlled from the boiler feed water cir. for coil power and add another branch circuit for the line/load side. If any one has seen what is typical set up for these (AND LEGAL) please let me know...
Thank You
Thank You