(180,180,150,150)=660
660 +(58.8 total fans)=
718.8 + (4.2 control) =
723 +(900 rpm 50 hp motor)
723+ 40.9= 763.9
Not sure about the 50 hp motor but the closes I could get to 763 total
(180,180,150,150)=660
The table note on top says min Circuit ampacity 1000 amps
705 ×175%= 1233.75Never mind I see what your doing the Asterix * means 763 without the pump motor or control kva so
(180+180+150+150) +25% largest
660 +45=705
705 +fans 58.8= 763.8
764 total RLA
180 x225% = 405I get a maximum OCPD size of 943A (= MCA + 100% largest RLA) if 440.22 applies,
Cheers, Wayne
Algebra:Where did you get that formula from?
In other words 225% -125%=100%Algebra:
A = 1.25 * x1 + x2 + x3 + etc
B = 2.25 * x1 + x2 + x3 + etc
Therefore
B - A = x1, or
B = A + x1
MOCP = MCA + (largest RLA/FLA) for HVAC equipment
For motors, the difference in coefficients is 1.25, so MOCP = MCA + 1.25*(largest motor FLA).
Cheers, Wayne