Looking for opinion on what to list as the actual running load for this chiller.
My thought is use the 172.8 kW/.8pf x 1.25 for a continuous kVA load.
It appears they established the minimum circuit ampacity of 323A by the following
172,800 / (480*1.73) = 207.8 /.8pf = 259.8 x 125% = 324A (they show 323A)
the .8pf was assumed as it is not listed on the cut sheet.
Curious what others think.
Thanks for looking
My thought is use the 172.8 kW/.8pf x 1.25 for a continuous kVA load.
It appears they established the minimum circuit ampacity of 323A by the following
172,800 / (480*1.73) = 207.8 /.8pf = 259.8 x 125% = 324A (they show 323A)
the .8pf was assumed as it is not listed on the cut sheet.
Curious what others think.
Thanks for looking